Current-transformer excitation current
ID: current-transformer-excitation-current
A current-transformer excitation current is the part of the secondary-referred input current needed for the magnetic core's response and losses rather than delivered to the external secondary circuit. In an ideal current transformer this contribution is neglected. In a real equivalent circuit it helps explain both current-transformer ratio error and current-transformer phase displacement.
Choose terminal polarities so ideal current reproduction is in phase. Let be the nominal primary-to-secondary ratio, the secondary-referred input phasor, and the measured secondary phasor. The current balance isRepresent the excitation branch locally by current-transformer excitation admittance and induced secondary phasor . With total secondary winding-plus-burden impedance ,The NIST treatment gives the corresponding magnetizing, leakage and burden equivalent circuit and shows how those impedances enter the complex ratio.[ref]
For an original local model, write with , and take . When ,The amplitude deficit is approximately , while the secondary lead is approximately radians. For stipulated , and , these are about and 5 milliradians. At an induced , the excitation components are 1 milliampere in phase and 5 milliamperes in quadrature; the real branch power is .
An increased current-transformer burden raises the induced potential required for a given secondary current. The actual excitation response need not remain linear: core behavior, frequency, waveform and prior magnetic state can change the local parameters. The NIST equivalent-circuit discussion explicitly notes the nonlinear core and current/burden dependence.[ref]
A proposed characterization varies a known connected burden and compares measured current ratio and phase, keeping the primary-current and frequency conditions recorded. A model that fits one operating point is not thereby validated through saturation or for arbitrary harmonic components. Separating excitation from load delivery explains why a turns ratio alone cannot specify practical measurement accuracy.