Current-transformer phase displacement

ID: current-transformer-phase-displacement

Current-transformer phase displacement is the phase difference between the secondary-current waveform and the corresponding primary-current waveform after accounting for the chosen terminal polarity. Define when the secondary reproduction leads the primary. NIST uses this sign convention and reports the angle directly; a positive amplitude correction factor does not specify the angle.[ref]
For sinusoidal signals, choose primary RMS phasor relative to a real supply phasor . Let the nominally scaled secondary reproduce
where is the current-transformer ratio error. A meter using this current and an otherwise exact supply measurement infers
For ,
A lag-defined phase error would have the opposite sign in the last term, so the convention must accompany the number.
For an original example, set , , , and radians. True active power is , while the current-shifted indication is about , an error of . At unity displacement power factor, the same phase displacement instead gives , a much smaller second-order effect. Low power factor makes phase characterization especially important for relative power accuracy.
At zero true active power, a relative-error ratio is undefined. For , the shifted indication is , which can be nonzero despite zero true average transfer. Report absolute error there rather than dividing by zero.
A proposed phase check compares the two current waveforms at the stated frequency, current level and current-transformer burden, with terminal direction and channel delay recorded. A time skew contributes a phase shift of magnitude ; at 50 Hz, 10 microseconds is about 3.142 milliradians. The measurement chain must distinguish that delay from the transformer itself. The NIST publication's historical calibration apparatus measured ratio and phase separately; the examples here are derived illustrations, not reported NIST performance.