A current transformer is a transformer used to reproduce a scaled version of an alternating primary electric current in a secondary measurement circuit. Many secondary turns around a primary with few turns make large primary electric currents measurable by an instrument. The DOE handbook describes this instrument arrangement and its magnetic operating conditions.[ref]
DOE Fundamentals Handbook Electrical Science. Volume 4, Module 13, Transformer Types, printed p.19, Instrument Current Transformer
For ideal magnitudes, primary and secondary turns giveThe polarity depends on the chosen terminal directions. The current-transformer burden is the connected secondary load, including the instrument and connection impedance. With a resistive secondary load , and its dissipated power is .
For an original example, take , , primary current RMS, and total secondary electrical resistance . The ideal secondary delivers , develops and supplies to this resistive burden. The reflected primary electrical resistance isThe primary is measured through magnetic coupling, while the secondary still needs a suitable connected circuit.
Real behavior includes current-transformer ratio error and current-transformer phase displacement. To see why the second matters, let the inferred current magnitude have fractional error and an extra lag relative to the true current. For a sinusoidal load with lag , the estimated-to-true active power ratio isWith , and radians, the first-order error is about . Correct amplitude scaling alone does not establish correct power measurement.
Opening an energized conventional current-transformer secondary removes its normal balancing current and can produce a large induced electric potential difference. The DOE handbook specifically explains this open-secondary behavior and its requirement for a closed secondary circuit when the instrument is absent.[ref]
DOE Fundamentals Handbook Electrical Science. Volume 4, Module 13, printed p.19, open-secondary explanation
A proposed measurement check therefore uses the intended connected burden and compares ratio and phase at relevant frequencies and current levels. Core response and saturation limit the ideal scaling model; a conventional inductive current transformer does not measure a steady DC component by the same transformer action. New to topics? Read the docs here!