Current-transformer ratio error

ID: current-transformer-ratio-error

Current-transformer ratio error quantifies the amplitude mismatch between primary electric current and the value inferred by multiplying secondary current by a nominal ratio. For positive RMS magnitudes and marked primary-to-secondary ratio , define the inferred-primary fractional error as
A negative value means that nominal scaling underestimates the primary current. This explicitly states the error convention; a reported correction can have the opposite sign.
The true ratio is . The current-transformer ratio correction factor used in NIST's report convention is
NIST distinguishes marked ratio, true ratio, ratio correction and ratio correction factor in its terminology section.[ref] Error and correction are approximately negatives for small errors, but their exact fractional relationship is nonlinear.
For an original example, take , a reference primary current of , and secondary current . Nominal scaling gives , so . The correction factor is . Multiplying the nominal indication by that factor recovers 500 A; simply adding 0.4% would leave a small second-order residual.
A simplified secondary-referred equivalent circuit makes burden dependence visible. Let divide between the measured secondary current and a current-transformer excitation current. With excitation admittance and total secondary series impedance ,
This original linearized model gives amplitude error approximately and phase shift approximately when . The core response can be nonlinear; the formula is not a universal calibration curve. NIST's equivalent circuit shows the separate magnetizing, leakage and burden terms that motivate such a model.[ref]
A proposed ratio test compares primary and secondary magnitudes against a reference at stated current, frequency and current-transformer burden. Record polarity and phase separately: a correct magnitude ratio does not establish a correct active power reading. The pair of ratio and current-transformer phase displacement measurements determines the relevant complex transfer at that operating point.