Current-transformer ratio error
ID: current-transformer-ratio-error
Current-transformer ratio error quantifies the amplitude mismatch between primary electric current and the value inferred by multiplying secondary current by a nominal ratio. For positive RMS magnitudes and marked primary-to-secondary ratio , define the inferred-primary fractional error asA negative value means that nominal scaling underestimates the primary current. This explicitly states the error convention; a reported correction can have the opposite sign.
The true ratio is . The current-transformer ratio correction factor used in NIST's report convention isNIST distinguishes marked ratio, true ratio, ratio correction and ratio correction factor in its terminology section.[ref]
A Calibration Service for Current Transformers by John D. Ramboz and Oskars Petersons. §1.3, printed pp.5–6, definitions and equations 3–4
Error and correction are approximately negatives for small errors, but their exact fractional relationship is nonlinear.For an original example, take , a reference primary current of , and secondary current . Nominal scaling gives , so . The correction factor is . Multiplying the nominal indication by that factor recovers 500 A; simply adding 0.4% would leave a small second-order residual.
A simplified secondary-referred equivalent circuit makes burden dependence visible. Let divide between the measured secondary current and a current-transformer excitation current. With excitation admittance and total secondary series impedance ,This original linearized model gives amplitude error approximately and phase shift approximately when . The core response can be nonlinear; the formula is not a universal calibration curve. NIST's equivalent circuit shows the separate magnetizing, leakage and burden terms that motivate such a model.[ref]
A proposed ratio test compares primary and secondary magnitudes against a reference at stated current, frequency and current-transformer burden. Record polarity and phase separately: a correct magnitude ratio does not establish a correct active power reading. The pair of ratio and current-transformer phase displacement measurements determines the relevant complex transfer at that operating point.