Power factor correction changes the current drawn from a source so that a specified active power is supplied with a more favorable power factor. For a sinusoidal inductive load, a parallel capacitor can supply an opposite reactive power component. It changes the source current's quadrature component while an ideal lossless correction branch leaves the load's active power unchanged.
Let the original load absorb at RMS potential difference and angular frequency . A parallel ideal capacitance contributes , soTo change a lagging phase angle from to a smaller lagging angle at fixed ,These follow from complex electrical power and the capacitive phase relationship.[ref]
AC Power Flow in Linear Networks by James L. Kirtley Jr.. Energy and Power, equations61–65; capacitive/inductive terms in equation71
For an original ideal example, take , and50Hz. An initial factor0.8 corresponds to750var. A target factor0.95 corresponds to about328.68var, so a capacitance about33.53µF supplies the difference. RMS source current changes from6.25A to about5.26A. Resistive feeder loss at fixed resistance changes by , while the1000W load conversion remains the same in this model.
Reactive power overcompensation occurs if the capacitive contribution exceeds the intended inductive component. The net then changes sign; continuing to add capacitance does not keep improving the magnitude of the factor. At a different load or frequency the same component can produce another result. Component ratings and nonideal circuit behavior require their own model rather than being determined by this one-frequency algebra.
Correction of displacement power factor is also distinct from correction of waveform distortion. Harmonic current can remain after the fundamental quadrature component is canceled. A useful measurement compares synchronized source potential-difference/current waveforms, RMS magnitudes and their average product before and after a change, retaining the operating condition. Separately measuring only RMS magnitudes cannot establish the resulting active power.